There should be no water in this SVP, it's purely to take bad gasses out through the roof so couple of condensing possibilities here.
Its cold in the loft (or should be) and the pipe wall probably chilly. Any warm air coming through the ceiling might be condensing on the outside of the pipe and dripping off at its lowest point.
The warm gas inside the pipe may be condensing on the inside of the cold pipe wall and running down the inside of the pipe to it's lowest point where it is getting out of a faulty joint.
Or the rain could be blowing up into the roof vent getting into the pipe and collecting in the bend.
Either way it would be a whole lot better if the SVP could be tilted up,fixed to the underside of the rafters and the vent taken much higher up the roof. The gas inside the SVP is warm, it wants to rise which means it willgo to the highest point of the pipe which, judging from the photos, is actually nearer the toilet than the roof.