[quote="Rsajackr"]I have just had a Sparky in and paid through the nose to have the Dist board changed and I thought £160 to drill 2 holes and clip 4 metres of cabling (supplied) and add a socket really taking the mickey. How hard can it be ??????
Please would you mind explaining IS NEUTRAL ON RCD NEUTRAL BAR ? in idiots speak?
Currently live to top of MCB, Neutral along side the others and the same with the earth. R'ds[/quote]
RSAJACKR
WITH A SPILT BOARD U HAVE 2 NEUTRAL BARS ONE FROM
THE MAIN SWITCH SIDE AND ONE FROM THE RCD SIDE.
SOMTIMES A RCD CIRCUIT NEUTRAL CAN BE BY MISTAKE
CONNECTED TO THE NEUTRAL BAR OF THE MAIN SWITCH
SIDE. TRIPPING OCCURS BECAUSE OF IMBALANCE
DETECTED ON RCD SIDE.
AVERAGE MAINS BOARD FROM £ 45 UP.
DEPENDING ON TIME TO INSTALL. ( LABOUR ON TOP )
THEN HE HAS 2 ISSUE CERTS AND NOTIFY HIS SCHEME PROVIDER 4 PART P TO COMPLY WITH AUTHORITYS PART P.
NOT A BAD PRICE. I ASSUME HE HAS ALSO RECTIFIED YOUR FAULT.