Oh I wish I could post pictures but this site is a pain for that. Anyway PME an TN-C-S are in most cases the same.
In the main the earth and neutral are the same wire until it reaches your house, Then they are split. A earth neutral fault needs 30 mA or more to point 15 ~ 30 mA to flow to earth to make it trip.
It is simple ohms law the main bit being the voltage. If there is zero voltage between earth and neutral then even a zero ohms short circuit will not cause any current to flow. There will be a resistance in the cables from the PME head to your consumer unit so a dead short will trip the RCD but much depends on current being drawn.
This is a real problem let me consider a real event and describe what happens.
A current has dislodged itself from a bun in the toaster. The current has landed between neutral and earth on the element and although not being used the switches only switch the line the neutral is still connected. The voltage between neutral and earth is zero so nothing trips.
The kettle is now used and the 3kW load means now there is a difference between neutral and earth. As a result enough current flows through the current to cause the RCD to trip.
To a casual observer it would seem the kettle is the problem where really it is the toaster causing the problem.
This is quite common and it has resulted in many a high power item being blamed when really the fault is in a low powered item.
With a RCD we really want all item to switch both lives. Neutral is considered as a live. Even as an electrician remembering the neutral is live and to call the phase wire line is hard.
The RCD is also called a ELCB-c or an Earth Leakage Circuit Breaker - Current. Before the ELCB-c we had the ELCB-v now outlawed which measured voltage instead of current. To work it measured the difference between house earth voltage and real earth voltage. The problem was if anything bonded the house earth to real earth it stopped working. As a result they were banned and the ELCB-c was used instead known also as a RCD.
At the end of the day what we want is for it to trip before we get a shock. And in the main it does that. OK where one touches a line wire it may take 40 ms before it disconnects but in the main that does not produce fatalities it may give us a wake up call to be more careful but does not kill us.