by ericmark »
Mon Apr 20, 2015 2:35 pm
Yes likely nothing to do with re-wire.
When a bulbs element ruptures it can either just cause a little spark and stop working or it can ionise the gases in the bulb when this happens you get a very bright flash and the built in fuse in the bulb should also rupture.
However the MCB is two devices built into one. And the magnetic part will normally work at 5 times rated value (B type) which is often lower that the current even if for a very short time that a bulb which ionises will draw. So it is common when moving from fuse to MCB to find the MCB trips when every bulb blows.
Today we buy most electrical stuff from China so the fuse may be missing.
The regulations say lighting must be 16 amp or less for fuse or MCB but often we use ceiling roses and junction boxes rated at just 5 or 6 amp so in real terms the MCB/Fuse should be either 5 amp for fuse or 6 amp for MCB. However many people put in larger units and the standard lamp holder is only rated at 2A so as a result if the fuse is missing from the lamp it can melt the contacts and mean you have to change holder as well.
Quartz bulbs are very bad and as a result you have to have a glass shield to stop the very hot quartz escaping when they blow.