by chris_on_tour2002 »
Sat Sep 27, 2008 5:11 pm
"am I correct in saying that the hot water from the heating also runs through a coil in the hot water cylinder to heat the water?"
yes, correct.
"when the heating is up to temp the top pipe to cylinder was hot and the bottom is cold"
firstly are you referring to the pipe at the very top of the cylinder? if so, this is not the heating coil, its your domestic supply. so you'd expect it to be piping hot when the hot water is on.
the pipe at the very bottom is the cold water feed from the tank in the attic. so you'd expect that to be stone cold.
the coil flow and return are usually found on the side of the cylinder, one about half way up and the other directly below it toward the bottom of the cylinder. check that you have identified the correct pipes first and if so:
do you have hot water? if so then it's probably not blocked. you would expect a temp difference between the two parts of the pipe - the coil works on heat exchange, hot water runs through the pipe, gives up it's thermal energy up to the water inside the cylinder thus is cooler on exit, then goes back to the boiler for reheating.
is the return part of the pipe stone cold whilst the flow is piping hot? this may indicate a blockage. but if your hot water is ok and heats up quite quickly then there is probably no blockage.