by htg engineer »
Fri Aug 10, 2007 2:28 pm
sounds like the actuator isn't working or the 3 port valve is sticking. This will be located just above the pump, or in the loft or airing cupboard etc.
Remove the motorised valve and select water only, and then heating only and see if the motorised valve turns, if not you need a new actuator, if it does turn, check the spindle on the 3 port valve is free to turn. Either way you'll probably need a new actuator because the motorised valve will be chewed where the spindle hasn't been turning.