RCCB snags
Ask questions and find answers to many subjects relating to electrics and electrical work

2 posts   •   Page 1 of 1
TimLouth
Labourer
Labourer
Posts: 1
Joined: Sun Mar 25, 2007 8:54 am

RCCB snags

by TimLouth » Sun Mar 25, 2007 9:01 am

I moved house last year and replaced the fuse box with a consumer unit. The socket rings and garage, shower and cooker circuits are all protected by an RCCB.
Every now and then the RCCB trips, it has happened about 8 or 9 times now. It happens every 10 days or so, though there is no real pattern to it. None of the MCCB's trip, except once when the socket ring went with the RCCB but this may have been a coincidence.
The last time the RCCB tripped was last night between 1 and 4 in the morning.
Have I got a duff RCCB, or is there anything I can do to try and track down the snag.
Any help or advice would be gratefully recieved.
Many thanks.

sparx
Project Manager
Project Manager
Posts: 2166
Joined: Wed Mar 21, 2007 8:33 pm
Location: The fifth continent.

by sparx » Sun Mar 25, 2007 10:02 pm

In a lifetime in the trade I have only ever had 2 out of spec RCCB's, an rcd tester will confirm if connected with all outgoing mcb's off, or an Earth leakage clamp meter around live & neutral tails, (not including Earth ). If niether available An insulation tester 'Megger' with all accessories in house UNPLUGGED should show a low I.R. fault which is what the RCCB is seeing, good luck, Sparx

2 posts   •   Page 1 of 1