by Sara H »
Wed Oct 15, 2008 11:34 pm
Ted
Whilst Ericmark is right with his statement about new installations having to incorporate RCD's or RCBO's to fall in line with the 17th Edition, you state that you are having a new supply fitted to an existing installation.
If what you are saying is correct and its a new supply (installed by an Electrical Service Provider) to the incoming main 100A or 80A fuse within your property the C/U (Consumer Unit) does not need to accomodate RCD's or RCBO's as your installation remains unchanged. Yes you may have to re-test the installation as the new cable may have a differing Ze to your previous cable but apart from that nothing else has to be improved.
If no board exists and the new supply is a total new board and installation then everything has to be in accordance with BS7671:2008 (17th Edition Wiring Regulations).
HTH
Sara