running drainage under the foor boards?
Drainage and wastage systems and plumbing help, advice and answers

4 posts   •   Page 1 of 1
sammyantha
Labourer
Labourer
Posts: 2
Joined: Sat Mar 14, 2009 9:08 pm

running drainage under the foor boards?

by sammyantha » Sat Mar 14, 2009 9:19 pm

hi i want to move a kitchen fro the back of the house to the front. the only problem is that there is not any drainage at the front only at the back of the house , can i run it through the house under the floors? the house is a terace house in the middle so cant run outside and around the side... Help

stoneyboy
Project Manager
Project Manager
Posts: 6536
Joined: Wed Dec 10, 2008 6:44 pm

by stoneyboy » Sun Mar 15, 2009 10:31 pm

sammyantha,
Provided you can get the necessary fall it will be OK. Make sure you fit an access T at the exit point so unblocking can be carried out if required.
end

sammyantha
Labourer
Labourer
Posts: 2
Joined: Sat Mar 14, 2009 9:08 pm

by sammyantha » Mon Mar 16, 2009 12:20 am

fantastic thank you, what is a necessary fall?

stoneyboy
Project Manager
Project Manager
Posts: 6536
Joined: Wed Dec 10, 2008 6:44 pm

by stoneyboy » Mon Mar 16, 2009 9:23 pm

sammyantha,
An absolute minimum would be 1 in 40, the problem you will have is supporting the pipe every 0.5m. You will also need to incorporate an Air Admitance Valve to prevent siphon action.
end

4 posts   •   Page 1 of 1
It is currently Fri Nov 29, 2024 10:40 pm