Sparkisi has told you exactly how the system works. When there is only a DHW demand the motorised valve (v4073a) is not energised,. The programmer supplies a voltage through the cylinder stat to the motorised valve. Thus either you have a faulty cylinder thermostat, programmer or wiring problem betw...
by BlueFlame
Mon Jul 02, 2007 1:48 pm
Forum: Central Heating and Air conditioning and Ventilation Forum
Topic: No hot water, CH ok
Replies: 17
Views: 9801

The v4073a is not energized when there is a HW demand. The valve is only energized for CH. When there is a DHW demand the sinal/voltage goes straight from the programmer to cylinder stat to boiler/pump. If the DHW is not working check cylinder stat and programmer are functioning correctly.