Post
by ericmark »
Mon Jan 09, 2017 11:40 pm
There are two sets of what one may call regulations. BS7671 and Part P, the latter is law, but BS7671 is not law but may be used in a court of law.
I did my apprenticeship in the late 1960's early 1970's and by that time journeyman had gone, my dad born 1924 did a journeyman that was year 6 and 7 of an apprenticeship. Well he actually never did it because of the war, he ended the war as a engine room artificer/chief petty-officer in Royal navy.
So I am assuming you are looking at BS7671 well I have 2008 but not amendment 3 so I may make some errors. But to summarise I will give some pointers.
One the ring final is a special, it needs to have a reasonably even load, as if the load is too close to the origin you can overload the 2.5mm sq cable. So the regulations suggest in the appendix any fixed appliance over 2 kW should have a dedicated supply.
Now it may seem strange but a outbuilding can be considered as a fixed appliance. So if the fused connection unit is fitted 1/3 to 2/3 around the ring final then even with a 13A fuse you are unlikely to draw more than 22 amp from either leg, but if close to the consumer unit it could.
You also have the RCD problem, a RCD FCU is the simple way out where there is no RCD in the consumer unit. With a 7 amp fuse in the FCU you are within the 2 kW limit.
The Part P varies according to if in England, or Wales, and there are other rules for Scotland. The English used is very poor, so it is hard to say exactly what is allowed. In England a new circuit needs permission and fees paid to LABC. However it seems they don't use the BS7671 definition and a FCU is not considered as forming a new circuit.
The word consumer unit means a type tested distribution unit. For an ordinary person in control you must use the type tested units, however if you are able to fit a distribution unit then you are not an ordinary person, you are instructed, or skilled, the competent person class has been removed from amendment 3 so no longer exists. So if you do anything to remove the type testing approval then it's not a consumer unit.
So in real terms Part P is important for rented accommodation, but in real terms can be ignored for owner occupier. Of course officially it is valid, but one is hardly likely to take ones self to court. And if planned before 2004 Part P is not valid. You should see all the plans I made!
So the main change was move from imperial to metric, 2.5mm is thinner than 28/0.014 cable so pre metric one was not that worried if the ring was broken, or if the loop impedance was exceeded, but with metric inspection and testing becomes important.
The ELI is not that important with RCD's and the line - neutral impedance is more linked to volt drop than ability to trip a B32 MCB. 105% of 5 x 32 amp = 168 amp and ohms law 230/168 = 1.37 ohms but volt drop with a incomer of 0.35 ohms means a loop impedance of around 1 ohm.
Also the RCD must trip at 5 x 0.030 amp in less than 40 mS which means test gear costing around £750 to buy, yes and a DIY'er is really going to buy it! So use common sense, but realise you can't possibly comply with the regs. So only do it with owner occupied.
Scotland is far stricter, and Wales is also more strict than England.