Hi agn Dougal, Most likely needs larger cable, isolator sw also may only be rated for 30A, 10.5 X 4.2A = 44.1 Amps so no wonder fuse melted!
If you are in England this is controlled service under part P of bldg regs so not DIY legally, regards SPARX