It is important as a 5a mcb will trip with a lower amps than a 5a fuse would.
Stick with it your doing ok, just that tripping and fusing in this case makes a difference.
A good elect or someone with a clamp on ammeter can tell you exact amps load with all lights on
Personally I dont think your over 5amps
WHEN you had two 5 amp trips they may only have had about 2 amp on each , now the two are together it could still be only 4amps ,as you obviously know, this would still be within your 5 amp mcb limit
As 5 amps is aprox 1200 watt this is the equivalent of about 18 sixty watt lamps before you overload it.
Your previous upstairs fuse with 4 sixty watt bulbs on would have only used about one amp.
Have you ever had to change the lamps , if so did you notice if the lampholders and any visible parts look burnt or anything.
When you say the bulb goes pop ,please expand
Does all the bulbs work up till the mcb trips and once reset that bulb no longer works.
If so is it the same bulb each time
or
Does the thing trip and on reset all bulbs are still working
Also
Does this occur when turning on that light
Or
How long is the light on before this happens
And how many times has this occured
Apoligies for all the questions but we are trying to advise how you can get this issue resolved
Regards R