toilet drain system.

by david somerville » Thu Mar 20, 2008 3:08 pm

I'VE BUILT AN EXTENTION ONTO MY HOUSE AND NOW INSTALLING A TOILET DOWNSTAIRS. NOT SURE WHAT THE SLOPE OF THE DRAIN PIPE GOING OUT OF THE HOUSE SHOULD BE. ie.FROM THE BACK OF THE TOILET PAN TO THE OUTSIDE WALL, THEN DOWN TO THE MANHOLE. CAN YOU HELP!
Last edited by david somerville on Fri Mar 21, 2008 2:51 pm, edited 2 times in total.

ALDA
Foreman
Foreman
Posts: 397
Joined: Mon Feb 04, 2008 8:15 pm

by ALDA » Thu Mar 20, 2008 4:49 pm

DAVID,

DEPENDS ON THE DIAMETER OF THE PIPE AND LENGTH OF THE PIPE FROM TOILET TO WHERE IT ENTERS VIRTICAL SOIL PIPE.

WHERE THE PIPE IS FOR SEWAGE ALONE A MODERATE FALL IS BETTER THAN A STEEP ONE.
THE LIQUID SHOULD NOT RUN AWAY LEAVING DEPOSITS TO FORM AND ADHERE TO THE DRAIN.(POTENTIAL FOR BLOCKAGES).

THERE IS A RULE OF THUMB METHOD OF DETERMINING THE FALL REQUIRED.
THAT IS, MULTIPLY THE DIAMETER OF THE PIPE IN INCHES BY TEN.
THEREFORE 100mm (4") PIPE NEEDS FALL OF 1 IN 40
150mm (6") PIPE NEEDS FALL OF 1 IN 60

HOPE THIS IS WHAT YOU ARE LOOKING FOR.

ALDA.