Cable Size and Amp Rating Identification
6 posts   •   Page 1 of 1
RobinClay
by RobinClay » Wed Feb 08, 2017 1:31 pm
It's easy enough to find size of cable for a particular rating, but what I want to know is - what is the rating of this cable ?
Somewhere there OUGHT to be a table of sizes vs. rating, but I've not been able to find one. The only tables talk about e.g. 2.5 mm for ring main cables - OK in theory, but totally useless in practice !
This particular cable is the old standard twin & earth, red, black & yellow/green (all sleeved), in an outer white PVC skin. The overall size, measured with calipers, is 14mm wide x 7mm thick. It's in a duct behind the render, then in the space between floorboards & ceiling.
So what's the rating of it ? Anyone ? Please ?
diydoctor
Re: Cable Size and Amp Rating Identification
by diydoctor » Wed Feb 08, 2017 6:01 pm
HI Robin
Although I'm not too sure what the rating of your particular cable would be, we do have a project covering size of cables and their ratings, hope this helps, if not now, maybe in the future: https://www.diydoctor.org.uk/projects/cablesizes.htm
Kind Regards
by ericmark » Thu Feb 09, 2017 1:59 am
Cable sizes have changed over the years, it was diameter and number of strands, now it's the cross sectional area. In real terms getting a micrometer on the cable does not work, what you want is some lugs, so red is 1 or 1.5 mm and blue 2.5 mm and yellow 4 or 6 mm and if slack or tight will show 4 or 6 mm. After that it's stamped on the lug.
Once you know the size the next step is type, some cable is rated 60 degs C normally flex, then 70 degs C standard twin and earth, (PVC) and 90 degs C for the like of ali-tube cable (LSZH). Mineral insulated can go even higher but the problem is even if the cable can run at 250 degs C at that temperature it would likely set other things on fire.
Then we have the route, there are letters to cover most routes, but twin and earth has 100, 101, 102, and 103 this http://www.batt.co.uk/upload/files/curr ... 876143.pdf link to Batt cables shows how 2.5mm cable can carry between 13.5 and 27 amp. For a ring final we need 20 amp cable so with 2.5mm either method 100 or 102 which limits insulation to no more than 100 mm thick. It also in the regulations shows how it should be clipped as if clipped to even a wooden beam that beam will help dissipate the heat.
Looking at the Batt cables spec it would seem you have 6 mm cable. But since you say white and earth is green/yellow not bare this could be wrong.
In free air or perforated cable tray 2.5mm LSZH cable can go up to 36 amp. This http://www.batt.co.uk/products/view/684 ... 00V-BS7211 is a link to that cable which is often white.
There are other manufactures but I tend to use Batt cables site myself. I really cringe when I go to places like B&Q and it says 2.5 mm is 21 amp cable, it's not that easy. We also need to compensate for heat and running cables together, but not really with domestic unless run with hot pipes.
RobinClay
by RobinClay » Thu Feb 09, 2017 11:39 am
Thanks, Doc !
Google sent me to that WebSite, but it doesn't answer my question, that's why I came on here ;-)
RobinClay
by RobinClay » Thu Feb 09, 2017 12:26 pm
Thank you, Eric !
My HAT but it's complicated !
Thank you for that explanation.
It's an existing cable that led to the cooker. We've replaced the cooker with a smaller one, and (of course) we "never" use ALL the rings & ovens at the same time ;-)
I have the opportunity now to replace the cable with a bigger one, but I think I C.B.A. ;-) It's served OK so far, all these years (I know not how many).
by ericmark » Thu Feb 09, 2017 5:56 pm
So it would seem 6mm was correct. I have questioned cooker cable size many times, although there has been a move to using 10mm cable, when using separate oven and hob the problem is you are only sure the oven is OK with a 32A feed, over that standard feed under fault conditions the internal wiring could fail before the fuse or MCB opens, so even with a 10mm cable using a MCB over 32A could cause problems.
What we need is a 16A fused connection unit for oven feeds, but they are simply not made.
It is currently Sun Nov 24, 2024 1:22 pm