Please help 2 Radiators not getting hot
mastermars
by mastermars » Fri Nov 23, 2007 8:46 am
Approx two years ago my boiler system was replaced with a combi type. Everything fine but one radiator in the system last year did not heat up despite bleeding it etc. I had to get a plumber who said the system needed balancing which he did and the radiator worked OK but only for a week or so. I never got the plumber back as this radiator was in a spare room. This year the central heating system has been turned on and this same radiator is cold but also another one, (both are upstairs as is the boiler), I have bleed them, but both were full. I have tried with all valves open on the other radiators and all valves closed but I cannot get any hot water feed to these two radiators. The hot water feed in pipe to the original radiator is just about warm but the feed to the second one remains stone cold. Is it possible there is a blockage somewhere?
peter the plumber
by peter the plumber » Fri Nov 23, 2007 10:04 am
On a combi boiler you need to have one radiator on all the time, normally the one in the bathroom.
This radiator should have a reduced flow, its only there to stop the boiler over heating if all the radiators are turn off.
I think this radiator is has its valves open too much, and you need to turn it down by one turn and see if that helps.
Its easy to find this radiator in your home, it will be the one without a TRV.
If you’re unlucky and they have fitted an auto bypass valve or differential bypass valve, you need to call someone in to check it and find the fault.
DONFRAMAC
by DONFRAMAC » Sun Dec 02, 2007 11:09 pm
If balancing the rad.with just IRV's ( bathroom or hall location common), try continuing balancing the rest of your rads. to put pressure onto the cool rads. If that doesn't work, then it is possible that your system needs flushing/rinsing to remove flushing chemicals/then refilling with a fresh charge of plain water dosed with corrosion-inhibitor. Unfortunately, it is not unusual for new systems to be installed without the above commissioning procedure being carried out, as it is so time-consuming.
Cleanser needs to be flushed out until all rads. drain out clear, as the chemical automatically becomes neutral after a few weeks and then all the flux & oil etc. taken into solution by it starts to precipitate out. Anti-corrosion additive is essential, especially now that aluminium is being used in boilers, and needs to be kept up to strength ;--- have it checked at the annual service.
I can personally vouch for this cowboy attitude existing in the trade, as my brand new system was left 10 days with plain water in it, and after complaining, they put both cleanser and inhibitor in together. They really do think the public are fools. Only a telephone call to the manufacturer of the chemicals clarified the required procedure. They are being recalled to flush the system fully, and recharge with inhibitor-doped water.