by ericmark »
Thu Apr 24, 2008 11:34 am
The fuse size can be given as Watts instead of amps and you need to divide the watts by 230 (volts) to get amps. And I should think any earth provided should be connected the question is should you have also fitted an earth mat over the heating wires? Section 753 of the wiring regulations covers underfloor heating. Here is one small bit of the regulation.
753.514 Identification and notices
The designer of the installation/heating system or installer shall provide a plan for each heating system, containing
the following details:
(i) Manufacturer and type of heating units
(ii) Number of heating units installed
(iii) Length area of heating units
(iv) Rated power
(v) Surface power density
(vi) Layout of the heating units in the form of a sketch. a drawing, or a picture
(vii) Position depth of heating Units
(viii) Position of junction boxes
(ix) Conductors, shields and the like
(x) Heated area
(xi) Rated voltage
(xii) Rated resistance (cold) of heating units
(xiii) Rated current of overcurrent protective device
(xiv) Rated residual operating current of RCD
(xv) The insulation resistance of the heating installation and the test voltage used
(xvi) The leakage capacitance.
This plan shall be fixed to, or adjacent to. the distribution board of the heating system.
Furthermore. the requirements of Figure 753 apply to floor and ceiling heating systems to inform the owner and the user of the installation.
As you can see quite involved and there is loads more like max temp and max wattage etc. I would be very careful that it does meet BS 7671:2008 before fitting.