Vaillant EcoTEC 837 NO FLOW OF HOT WATER!
All aspects of plumbing questions and answers, help, tips and information

3 posts   •   Page 1 of 1
Lectrician
Labourer
Labourer
Posts: 1
Joined: Sun Mar 09, 2008 6:51 pm

Vaillant EcoTEC 837 NO FLOW OF HOT WATER!

by Lectrician » Sun Mar 09, 2008 6:52 pm

I drained down my rads to add another, and have refilled the system.

I put the boiler into test mode 0 (CH and DHW bleeding) instead of 6 (filling).

The rads are all working fine, and warming up, but I open the HW taps and there is just no flow at all - nothing.

I had this happen last time I drained down and re-filled, and cannot remember what I did to cure it?!?

How and why does the boiler prevent any flow to the taps?

Cheers.

sjlheating
Labourer
Labourer
Posts: 4
Joined: Sun Mar 09, 2008 9:29 pm

by sjlheating » Sun Mar 09, 2008 9:31 pm

the filling on this combi is by using the same isolation valve as the cold water inlet isolation so i would guess u haven't opened the cold inlet correctly under the boiler

sjlheating
Labourer
Labourer
Posts: 4
Joined: Sun Mar 09, 2008 9:29 pm

by sjlheating » Sun Mar 09, 2008 9:34 pm

sorry ...read that back and it didnt sound to clear.!
if your boiler has an internal filling system ( as apposed to a filling loop added at installation) u have probably turned it the wrong way after filling your central heating. this isolates the cold feed to the combi..hence no hot water comes out of the taps!! thanks

3 posts   •   Page 1 of 1
It is currently Tue Nov 26, 2024 11:00 pm