by sparx »
Wed Feb 04, 2009 9:10 pm
Hi again,
yes that would be fine to fit in place of existing socket on a 6mm cable as you say 35A fuse? are you sure it's not a 32A ? 35's an odd size.
As for load, 10.3 kW is around 44A but as I explained on another posting recently, their is an allowance in the regs for 'diversity' on cooker circuits which says you take:
10% of total ie 4.4A plus 30% of remaining load ie
[44-4.4] = 39.6A/30%= 13.07 + 5A for socket on panel, so total assumed load = 4.4+13.07+5=22.47A, well within your supply.
'On site guide' gives rule of thumb that any cooker up to 15,000w can run from a 32A cooker circuit,
regards SPARX