by Jeffmo »
Mon May 28, 2007 1:41 pm
Hi John , with regards to 1st ? , the shower will require an RCD , this can go either 2 ways i.) A seperate RCD outside the consumer unit (Fuse Box)
ii.) If the consumer unit is already a split load board and there is a spare way in there on the protected side then you just need the correct MCB fitting . (Remember this is part p work and should be done by a qualified and certified electrician )
Secondly as regards supplementary bonding , this is a requirement to bond your water pipes that could possibly become live , the supplementary bonding should be taken from the water pipe ( that connects to shower) with 4mm earth cable , this can then be connected either to a spur or socket ( outside the room with the shower) . Tis ensures that all pipework is earthed. Hope this helps . Don't know where the 10 mm earth wire comes into it though . Any more info would be helpfull .Regards Jeff