by kbrownie »
Thu Jan 24, 2013 8:15 pm
You will need to run a twin and earth cable form the hall light fitting, connecting the brown of twin and earth to the live side of light (not the loop in) and the blue to the neutral side of light of both hall way and external light.
Don't forget to install and terminate the earth cable and prove there is continuity of this conductor back to the consumer unit. The earth cable cable will require sleeving with Green&Yellow PVC sleeve.
Not sure why you want to do this though and not have separate functional switch for external light.
I personally would always recommend that outside equipment being taken off internal circuits are protected by double pole switches, to prevent total power loss of the circuit if an external fault occurs.