Earth bonding.
Ask questions and find answers to many subjects relating to electrics and electrical work

5 posts   •   Page 1 of 1
DEEARR2
Ganger
Ganger
Posts: 160
Joined: Sun Oct 12, 2008 9:49 pm

Earth bonding.

by DEEARR2 » Tue Sep 29, 2009 10:25 pm

Can anyone please confirm or deny the need to earth bond all pipe work surrounding a gas central heating boiler. I have been told that the cross bonding of all three incoming services is sufficient and that all electrical components in the boiler are individually earthed, :?:
Help please as I am not convinced by this statement.

kbrownie
Project Manager
Project Manager
Posts: 1995
Joined: Mon Mar 05, 2007 9:36 pm

by kbrownie » Wed Sep 30, 2009 11:28 am

Your incoming gas and water supply should be bonded to the MET at the Consumer unit.
There is a metal plate that links all pipework (incoming and outs) on the underside of most boilers.
So this should cause continuity as far as your main earth bonding is concerned.
KB

steve the plumber
Ganger
Ganger
Posts: 72
Joined: Mon May 04, 2009 10:32 pm

by steve the plumber » Wed Sep 30, 2009 1:30 pm

I always earth all pipes.

sparx
Project Manager
Project Manager
Posts: 2166
Joined: Wed Mar 21, 2007 8:33 pm
Location: The fifth continent.

by sparx » Wed Sep 30, 2009 10:28 pm

as KB says there is no requirements under electrical regs. but Corgi/gasafe may insist on it for their installers, in a similar way that NICEIC want fly/pigtail earths in back boxes, also not a requirement of regs. if wiring with a CPC.

[If a qualified electrician, rather than a plumber wishes to argue then please quote relevent reg. #]

regards Sparx

DEEARR2
Ganger
Ganger
Posts: 160
Joined: Sun Oct 12, 2008 9:49 pm

Earth Bonding

by DEEARR2 » Thu Oct 01, 2009 5:41 pm

Thanks for you input guys, feel safer allready.

5 posts   •   Page 1 of 1
It is currently Fri Jan 17, 2025 11:40 pm