Ring Main problem
davidb174
Ring Main problem
by davidb174 » Fri Jun 15, 2007 3:25 pm
I have an annoying ring main fault. We have a consumer unit with RCD's. Every so often two of the RCD's trip, the 15A and 30A. They refuse to reset until approximately 10 to 12 hours later. The unit wil then be fine for some weeks then will trip again. I have checked all the appliances connected to the circuit and can detect no fault with these. It seems the fault is with the ring main circuit itself?
BLAKEY1963
Re: Ring Main problem
by BLAKEY1963 » Fri Jun 15, 2007 7:34 pm
[quote="davidb174"]I have an annoying ring main fault. We have a consumer unit with RCD's. Every so often two of the RCD's trip, the 15A and 30A. They refuse to reset until approximately 10 to 12 hours later. The unit wil then be fine for some weeks then will trip again. I have checked all the appliances connected to the circuit and can detect no fault with these. It seems the fault is with the ring main circuit itself?[/quote]
DAVID
IF YOU UNPLUG ALL CURRENT USING APPLIANCES AND ARE
CONVINCED THE PROBLEM IS ON THE RING MAIN WIRING ITSLEF,
YOU NEED TO GET A REGISTERED ELECTRICIAN IN TO TEST THE
CIRCUIT, PERFORMING CONTINUITY OF R1 + R2 AND THE NEUTRAL
CONDUCTOR , POLARITY CHECKS, AND INSULATION RESISTANCE
TESTS . A CONDITION CAN THEN BE ASSESSED OF THE CIRCUIT
TO SEE WHETHER IT IS FAULTY OR NOT
BLAKEY 1963
It is currently Sat Sep 19, 2026 3:13 am