No Earth in light switch

by Lawrence » Sun May 27, 2007 5:18 pm

I've been putting up a surface mounted light switch using a standard plastic back box. As there's nowhere to fix the earth from the switch wire presmably you just put some green/yellow sleeving on it and leave in the box?

When you do the radial circuit continuity and insulation tests doesn't this give odd results?

pdenni
Apprentice
Apprentice
Posts: 15
Joined: Thu May 24, 2007 7:43 pm

by pdenni » Sun May 27, 2007 7:43 pm

hello

yes you are correct you sleeve the earth and put it an a connector block, it doesn't have any impact on test results.

Jeffmo
Ganger
Ganger
Posts: 103
Joined: Mon Apr 09, 2007 10:22 am

by Jeffmo » Sun May 27, 2007 8:24 pm

hi , if there is an earth connection in the pattress ( box) then use that , if not just sleeving it is not good , so fit with connector block after sleeving ofcourse. Cheers Jeff

sparx
Project Manager
Project Manager
Posts: 2166
Joined: Wed Mar 21, 2007 8:33 pm
Location: The fifth continent.

by sparx » Sun May 27, 2007 9:35 pm

Hi Lawrence, about right but if room put small term block on to make sure not able to touch conn.
No prob with any testing as it's only a 'tee' off main circuit, so continuity will go through light to light, and I.R. tests won't be affected either as long as kept away from other wires as I said ,
regards SPARX